QUESTION 10.6.2

Low-flashpoint-fuel bunkering ESD system

Oil, Chemical, LPGCargo Manifold

What is being checked

The inspector is checking whether ship and bunker-source ESD functions, communications and shutdown links stop transfer and isolate fuel safely when a hazardous condition occurs.

Ready onboard

0/6 complete

Practice questions

Answer aloud, then open the preparation point.

1What conditions automatically activate ESD?

Use the vessel cause-and-effect matrix and identify the actual gas, fire, level, power and link failures configured.

2What happens on the bunker vessel or terminal when you press ESD?

Explain the tested linked response, including remote pump stop, valve actions and communications.

3How is pressure surge controlled?

Coordinate valve closing time, pump trip and transfer-system design within the approved compatibility study.

4Can ESD be reset immediately after a false alarm?

No. Identify the initiating cause, confirm safe conditions and obtain ship-shore agreement before controlled reset and restart.

5What if the primary ESD link is incompatible?

Use only an approved alternative established by the compatibility and risk assessment; do not begin with an untested improvised link.

Where an observation may arise

LINK UNTESTED

Transfer starts without proving both sides of the ESD connection.

CAUSE UNKNOWN

Crew cannot explain automatic initiators and resulting actions.

MANUAL ACCESS

An ESD point is blocked, unlabelled or defective.

SURGE RISK

Closing sequence or time is incompatible with the transfer arrangement.

UNCONTROLLED RESET

The system is reset without determining the cause or joint approval.

Master's practical note

Require both sides to state what will move when ESD is activated. A successful lamp test is not proof that the remote pump and isolation valves will respond together.

Equipment boundary and references

Equipment boundary: This applies only where the scoped vessel uses LNG or another low-flashpoint fuel. ESD compatibility and closing-time criteria must follow the approved ship and supplier transfer design.

References

  • OCIMF SIRE 2.0 Question Library Part 2, Version 1.0, Question 10.6.2
  • IGF Code Part A-1 chapters 8 and 15
  • ISO 20519
  • SGMF LNG bunkering guidance
  • ISO 21593 where applicable

Last reviewed: 2026-09-10