Maritime analysis. Real-time insight.

QUESTION 8.3.7

Inert-gas oxygen analyser

Oil, ChemicalEngine Control Room, Cargo Control Room, Engine Room

What is being checked

The inspector is checking whether the inert-gas oxygen analyser and associated sampling arrangement matches the approved arrangement, is physically ready, is tested through its complete operating path and is understood by responsible personnel.

Ready onboard

0/6 complete

Practice questions

Answer aloud, then open the preparation point.

1What is the purpose and operating limit of the inert-gas oxygen analyser and associated sampling arrangement?

Explain the protection provided by sampling point, conditioning, calibration gases, alarm and shutdown set points, recorder, span and zero checks, including the condition that requires intervention.

2How is the complete operating path tested?

Use the approved safe test method to prove zero and span response, sample flow, high-oxygen alarm, shutdown and comparison with a verified portable analyser, including the final alarm, trip, movement or indication.

3What happens if the equipment is unavailable?

Notify the Master and terminal as applicable, stop or restrict the affected operation, establish approved compensating controls and obtain repair or formal authority.

4Show the latest maintenance and defect history.

Match the physical identity to PMS, calibration or service records and verify that any temporary control has been closed.

5Which indication proves the equipment is in its safe condition?

Identify the local and remote indication, its source, alarm set point and how a false or frozen signal would be detected.

Where an observation may arise

ARRANGEMENT CONFLICT

The fitted system, drawing, manual or certificate did not agree.

PHYSICAL DEFECT

Inspection identified expired gas, blocked sample, leaking line, wet sensor, wrong set point, drift or bypassed alarm.

INCOMPLETE TEST

Records did not prove zero and span response, sample flow, high-oxygen alarm, shutdown and comparison with a verified portable analyser through the complete operating path.

ALARM DEFECT

An alarm, trip, interlock or indication was isolated, incorrect, overdue for test or not understood.

MAINTENANCE GAP

PMS, calibration, service or repair evidence was missing, overdue or not traceable to the item.

KNOWLEDGE GAP

Responsible personnel could not explain sampling point, conditioning, calibration gases, alarm and shutdown set points, recorder, span and zero checks, operating limitations or failure response.

Master's practical note

Trace one signal or flow path from the field device to the CCR or ECR and back to the final protective action. A successful local test alone may not prove the full system.

Equipment boundary and references

Equipment boundary: Use approved test modes and maker instructions. Do not bypass an interlock, release cargo or defeat protection merely to satisfy an inspection demonstration.

References

  • OCIMF SIRE 2.0 Question Library Part 2, Version 1.0, Question 8.3.7
  • SOLAS Chapter II-2 regulation 4.5.5
  • IMO FSS Code Chapter 15

Last reviewed: 2026-09-14