QUESTION 10.7.2

Preventing oil spray onto hot machinery surfaces

Oil, Chemical, LPG, LNGEngine Room

What is being checked

The inspector is checking whether hot surfaces are insulated below ignition-risk temperatures and flammable-oil systems are shielded, jacketed and maintained so a leak cannot produce an engine-room fire.

Ready onboard

0/7 complete

Practice questions

Answer aloud, then open the preparation point.

1What surface-temperature limit is used for fire prevention?

SOLAS controls exposed surfaces above 220 C that may be impinged by a flammable-system failure; apply the vessel survey and insulation standard.

2Why must oil-soaked lagging be replaced?

Oil retained inside insulation can reach a hot surface and ignite even when the outer cladding looks clean.

3How are hot spots found?

Conduct a representative-load thermal survey and combine it with close inspection of missing cladding, joints and shield condition.

4What is the purpose of jacketed fuel pipes?

The outer pipe captures high-pressure leakage and leads it to a drain or alarm rather than allowing atomised spray.

5Which recent maintenance can create new risk?

Disturbed exhaust insulation, misaligned shields, loose fuel fittings and blocked leak-off pipes require post-work inspection and load verification.

Where an observation may arise

EXPOSED HOT SPOT

A surface above the applicable threshold lacks effective insulation.

OIL-SOAKED LAGGING

Contaminated insulation remains in service or is concealed by new cladding.

SPRAY PATH

A pressurised fuel or lubricating-oil joint can discharge onto a hot surface.

JACKET DEFECT

Double-wall piping, leak collection or alarm is incomplete or blocked.

ACTIVE LEAK

Oil seepage is accepted or caught by an improvised container.

SURVEY GAP

Temperature checks are absent, outdated or conducted only at low load.

Master's practical note

Inspect after recent work and at representative load. Fires often begin where insulation or spray shielding was disturbed during otherwise successful maintenance.

Equipment boundary and references

Equipment boundary: The 220 C criterion comes from SOLAS fire-prevention requirements, but lower-temperature risks and maker limits still require control. Thermal imaging does not replace physical inspection beneath suspect cladding.

References

  • OCIMF SIRE 2.0 Question Library Part 2, Version 1.0, Question 10.7.2
  • SOLAS Chapter II-2 regulation 4.2.2.6
  • IMO MSC.1/Circ.1321
  • IACS UR M15
  • Manufacturer instructions

Last reviewed: 2026-09-10