Remote shutdowns and quick-closing oil valves
What is being checked
The inspector is checking whether remote fuel and lubricating-oil isolation and pump shutdowns can remove the source of a machinery-space fire, and whether crew know the correct sequence and consequences.
Ready onboard
0/6 completePractice questions
Answer aloud, then open the preparation point.
1Which controls would you operate for a purifier-room fire?
Identify the relevant fuel supply and transfer pumps, tank quick-closing valves, ventilation and other controls from the vessel plan and emergency procedure.
2Why must a quick-closing valve be reset locally?
It prevents remote or inadvertent restoration of fuel into a space that may still be unsafe.
3How is a valve tested without stopping essential machinery?
Use the approved staggered or partial test and verify actual closure at a safe opportunity, with risk and plant status controlled.
4What propulsion consequence follows closing these valves?
State which service, settling or lubricating-oil supplies are isolated and how that affects main and auxiliary machinery.
5How do you know the label is correct?
Trace the control physically or through approved drawings and confirm it during the functional-test record.
Where an observation may arise
A remote handle or stop does not identify the actual equipment controlled.
The release operates but the valve does not reach the closed position.
The remote-control station cannot be reached promptly.
Crew would isolate the wrong tank, pump or essential system.
The arrangement allows uncontrolled restoration from outside the space.
Records show visual checks without proving closure or shutdown.
Master's practical note
Do not stop at pulling the release. Verify which valve or motor actually moved and whether the label, drawing and operational consequence agree.
Equipment boundary and references
Equipment boundary: Testing must preserve propulsion, electrical and safety-system availability. Follow the approved test method and never reopen oil supply remotely into an unverified fire area.
References
- OCIMF SIRE 2.0 Question Library Part 2, Version 1.0, Question 10.7.1
- SOLAS Chapter II-2 regulation 4
- IMO MSC.1/Circ.1321
- ISM Code section 8
Last reviewed: 2026-09-10