Maritime analysis. Real-time insight.

QUESTION 8.4.5

IGC Code emergency escape sets

LPGEngine Room, Interview - Rating, Internal Accommodation

What is being checked

The inspector is checking whether the complete arrangement for IGC Code emergency escape respiratory protection meets the cargo-code requirement, remains immediately usable and is understood by the personnel assigned to use it.

Ready onboard

0/6 complete

Practice questions

Answer aloud, then open the preparation point.

1Why is this scale of IGC Code emergency escape respiratory protection required?

Relate escape sets for each person and additional sets at the locations required by the approved arrangement to the cargo code, Certificate of Fitness, muster duties and vessel arrangement.

2How do you check it before use?

Check completeness, suitability, service status and the defects most likely to prevent protection: expired unit, low pressure, damaged hood, broken seal, inaccessible location or wrong distribution.

3How is it used safely?

Demonstrate or explain rapid donning, activation and escape while recognising that an escape set is not for firefighting or cargo-space entry, including withdrawal and decontamination limits.

4What if an item is defective or missing?

Replace it with an equivalent approved item, control affected cargo work and record the defect and restoration.

5How do you confirm compatibility with today's cargo?

Use the Certificate of Fitness, cargo SDS and maker limitations rather than relying on colour or general familiarity.

Where an observation may arise

INSUFFICIENT SCALE

The inventory did not provide the required arrangement for escape sets for each person and additional sets at the locations required by the approved arrangement.

POOR CONDITION

Inspection identified expired unit, low pressure, damaged hood, broken seal, inaccessible location or wrong distribution.

WRONG PROTECTION

The equipment material, cartridge, cylinder or clothing was unsuitable for the cargo hazard.

SERVICE OVERDUE

Testing, service, calibration or replacement was overdue or not traceable.

INACCESSIBLE

Required equipment was obstructed, unmarked or stored where contamination could prevent access.

CREW KNOWLEDGE

Assigned personnel could not explain rapid donning, activation and escape while recognising that an escape set is not for firefighting or cargo-space entry.

Master's practical note

Select equipment from the station closest to the cargo risk, not only the best-maintained locker. The weakest required set determines actual readiness.

Equipment boundary and references

Equipment boundary: Use training or demonstration equipment where available. Do not consume filters, break seals or impair emergency equipment solely for inspection.

References

  • OCIMF SIRE 2.0 Question Library Part 2, Version 1.0, Question 8.4.5
  • IMO IGC Code Chapter 14
  • IMO FSS Code Chapter 3

Last reviewed: 2026-09-14