QUESTION 5.2.6

Machinery-space pressure water-spray system

Oil, Chemical, LPG, LNGEngine Control Room, Engine Room, Emergency Headquarters.

What is being checked

The inspector is checking whether officers understand the location, coverage, release logic and limitations of the fixed pressure water-spraying system, and whether testing and physical condition prove that it will operate without endangering personnel.

Ready onboard

0/6 complete

Practice questions

Answer aloud, then open the preparation point.

1What area is protected by the fixed pressure water-spraying system?

Trace the approved plan and physically identify boundaries, sections, exclusions and the location from which the system is released.

2What must happen before release?

Account for personnel, raise alarms, isolate ventilation and fuel or machinery as required, then operate pump start, sectional valves, distribution piping, nozzles, alarms and protected equipment in the approved sequence.

3How is the system tested without discharging extinguishing medium?

Use the approved simulation or sectional test and show pump, pressure, section, alarm and representative nozzle-flow tests, including alarms, interlocks and remote indications.

4What if part of the system is unavailable?

Notify the Master and shore, establish fire watch or equivalent compensating measures, restrict operations if necessary and obtain repair or formal authority.

5What is the principal failure risk?

Identify and control blocked nozzles, corroded piping, closed section valves, inadequate pressure or ineffective spray coverage.

Where an observation may arise

KNOWLEDGE GAP

Responsible officers could not explain coverage, release sequence, safety interlocks or limitations.

INACCESSIBLE CONTROL

A release station, valve, pump or isolation was obstructed, unlabelled or unavailable.

INCOMPLETE TEST

Records did not prove the complete path, including pump, pressure, section, alarm and representative nozzle-flow tests.

PHYSICAL DEFECT

Inspection identified blocked nozzles, corroded piping, closed section valves, inadequate pressure or ineffective spray coverage.

UNAUTHORISED ISOLATION

A valve, power supply, alarm or automatic function was isolated without formal control.

IMPAIRMENT UNCONTROLLED

A known defect had no effective compensating measure or repair plan.

Master's practical note

Ask the officer to trace the release from the control handle to the protected space. Familiarity with a poster is insufficient if the person cannot identify the actual shutdowns, valves and confirmation indications.

Equipment boundary and references

Equipment boundary: Demonstrations must use the approved test mode. Never discharge extinguishing medium or defeat a safety interlock solely for inspection.

References

  • OCIMF SIRE 2.0 Question Library Part 1, Version 1.0, Question 5.2.6
  • SOLAS Chapter II-2 regulation 10
  • IMO FSS Code Chapter 7

Last reviewed: 2026-09-13