Fixed fire detection and alarm system
What is being checked
The inspector is checking whether officers understand the location, coverage, release logic and limitations of the fixed fire-detection and alarm system, and whether testing and physical condition prove that it will operate without endangering personnel.
Ready onboard
0/6 completePractice questions
Answer aloud, then open the preparation point.
1What area is protected by the fixed fire-detection and alarm system?
Trace the approved plan and physically identify boundaries, sections, exclusions and the location from which the system is released.
2What must happen before release?
Account for personnel, raise alarms, isolate ventilation and fuel or machinery as required, then operate detector zones, panel functions, alarm transfer, fault monitoring and power supplies in the approved sequence.
3How is the system tested without discharging extinguishing medium?
Use the approved simulation or sectional test and show detector activation, zone indication, audible and visual alarms, fault and standby-power tests, including alarms, interlocks and remote indications.
4What if part of the system is unavailable?
Notify the Master and shore, establish fire watch or equivalent compensating measures, restrict operations if necessary and obtain repair or formal authority.
5What is the principal failure risk?
Identify and control inhibited detectors, wrong zone identification, panel faults, delayed alarm transfer or missing test equipment.
Where an observation may arise
Responsible officers could not explain coverage, release sequence, safety interlocks or limitations.
A release station, valve, pump or isolation was obstructed, unlabelled or unavailable.
Records did not prove the complete path, including detector activation, zone indication, audible and visual alarms, fault and standby-power tests.
Inspection identified inhibited detectors, wrong zone identification, panel faults, delayed alarm transfer or missing test equipment.
A valve, power supply, alarm or automatic function was isolated without formal control.
A known defect had no effective compensating measure or repair plan.
Master's practical note
Ask the officer to trace the release from the control handle to the protected space. Familiarity with a poster is insufficient if the person cannot identify the actual shutdowns, valves and confirmation indications.
Equipment boundary and references
Equipment boundary: Demonstrations must use the approved test mode. Never discharge extinguishing medium or defeat a safety interlock solely for inspection.
References
- OCIMF SIRE 2.0 Question Library Part 1, Version 1.0, Question 5.2.3
- SOLAS Chapter II-2 regulation 7
- IMO FSS Code Chapter 9