Maritime analysis. Real-time insight.

QUESTION 5.2.1

Emergency fire-pump starting and supply

Oil, Chemical, LPG, LNGSteering Gear, Aft Mooring Deck

What is being checked

The inspector is checking whether officers understand the location, coverage, release logic and limitations of the emergency fire pump, and whether testing and physical condition prove that it will operate without endangering personnel.

Ready onboard

0/6 complete

Practice questions

Answer aloud, then open the preparation point.

1What area is protected by the emergency fire pump?

Trace the approved plan and physically identify boundaries, sections, exclusions and the location from which the system is released.

2What must happen before release?

Account for personnel, raise alarms, isolate ventilation and fuel or machinery as required, then operate remote or local start, suction arrangement, priming and discharge valve alignment in the approved sequence.

3How is the system tested without discharging extinguishing medium?

Use the approved simulation or sectional test and show start tests, pressure at the hydraulically most remote hydrants and pump-room checks, including alarms, interlocks and remote indications.

4What if part of the system is unavailable?

Notify the Master and shore, establish fire watch or equivalent compensating measures, restrict operations if necessary and obtain repair or formal authority.

5What is the principal failure risk?

Identify and control failure to prime, frozen or closed suction, leakage, inadequate pressure or an inaccessible pump space.

Where an observation may arise

KNOWLEDGE GAP

Responsible officers could not explain coverage, release sequence, safety interlocks or limitations.

INACCESSIBLE CONTROL

A release station, valve, pump or isolation was obstructed, unlabelled or unavailable.

INCOMPLETE TEST

Records did not prove the complete path, including start tests, pressure at the hydraulically most remote hydrants and pump-room checks.

PHYSICAL DEFECT

Inspection identified failure to prime, frozen or closed suction, leakage, inadequate pressure or an inaccessible pump space.

UNAUTHORISED ISOLATION

A valve, power supply, alarm or automatic function was isolated without formal control.

IMPAIRMENT UNCONTROLLED

A known defect had no effective compensating measure or repair plan.

Master's practical note

Ask the officer to trace the release from the control handle to the protected space. Familiarity with a poster is insufficient if the person cannot identify the actual shutdowns, valves and confirmation indications.

Questions reported during inspections

Anonymised user reports, not official OCIMF questions or a prediction of what an inspector will ask.

HardwareReported inspection question

The discharge pressure gauge of the emergency fire pump located in steering gear room indicated a pressure of 3.5 bars with the pump in stopped condition.

Oil tanker · Both / common · Engine room / ECR

Equipment boundary and references

Equipment boundary: Demonstrations must use the approved test mode. Never discharge extinguishing medium or defeat a safety interlock solely for inspection.

References

  • OCIMF SIRE 2.0 Question Library Part 1, Version 1.0, Question 5.2.1
  • SOLAS Chapter II-2 regulation 10

Last reviewed: 2026-09-13